EmbDev.net
Forum: FPGA, VHDL & Verilog FPGA IIR Filter and High Pass
Du wurdest von Mikrocontroller.net auf diese Seite weitergeleitet. Zurück zu Mikrocontroller.net
von Marcel D. (diablokiller999)
Rate this post
useful
not useful
Hi guys!
I've written another IIR implementation after Directform 1 to implement
a high pass filter in my current design, the IIR will be combined with a
CIC that downsamples the sampling rate from 10MHz to ~79KHz. My filter
coefficients for the IIR are as follows:
> A1 = -1,93178
> A2 = 0,93403
> B0 = 0,96645
> B1 = -1,93291
> B2 = 0,96645
The coefficients are scaled by 2^30 and then divided by this value after
the multiplication. My implementation works with 4 guard bits, as you
can see Idle-State for nX0.
Although my simulation looks OK (to me), it doesn't work in the real
FPGA so frequencies below 1KHz are still in the signal. How do I
properly test my IIR and is there maybe something I'm missing in my
implementation?
von Bernhard K. (bkom)
Rate this post
useful
not useful
maybe I don't see it but somehow I miss a statement like:
 "if rising_edge(iclk) then" or " wait until rising_edge(iclk);"
 in your VHDL...
process(iCLK,iRESET_N)
begin
    if(iRESET_N = '0') then
        nZX0                <= (others => '0');
        nZX1                <= (others => '0');
        nZX2                <= (others => '0');
        nYOUT               <= (others => '0');
    else
//-->>>  e.g.: if rising_edge(iclk) then
        case state is
examples here:
https://stackoverflow.com/questions/32717040/wait-until-rising-edgeclk-vs-if-rising-edgeclk
Rate this post
useful
not useful
>  in your VHDL...
Holy crap you're right!
Some code-blindness >_>
I'll compile again and report if this was my (really) stupid mistake :D
: Edited by User
Rate this post
useful
not useful
So I've implemented the clocked version :D
I did a test on the filter via an 1V amplitude and a frequency sweep
from 0 to 3000Hz. It seems to filter a bit, but not nearly as good as
I've simulated.
It looks that I'm missing something, the curve looks like I'm on track
but is my division flawed at some point?
: Edited by User
von Thomas R. (Company: abaxor engineering) (abaxor)
Rate this post
useful
not useful
1. You should sum up the multiplication results and not the truncated
multiplication results. Using the truncated values will increase
rounding noise.
2. probably this line will lead to a timing violation:
  nYOUT      <=
std_logic_vector(signed(nDX0)+signed(nDX1)+signed(nDX2)-signed(nDY1)-sig
ned(nDY2));
Tom
Rate this post
useful
not useful
> rounding noise.
Done, values are a bit different and simulation looks ok, the curve
looks identical. Will try this in my FPGA, new code and testbench are
added if someone wants a closer look.
>   nYOUT      <=
ned(nDY2));
According to Quartus it seems OK though, no timing problems mentioned by
TimeQuest.
Rate this post
useful
not useful
So far I've made two versions of the IIR, one is more async
(IIR_Biquad_II.vhd) and one uses a state machine (IIRDF1.vhd). The more
async one was derived from a project on the internet and it seems to
work as a high pass (but gives a weird curve as low pass). I've
implemented both in the FPGA and the async gives a really nice curve,
while the one with the state machine has some weird effects. Can someone
tell me why this is? I really have no clue what should cause this :-/
By the way, my own state machine implementation works fairly well as a
low pass, as you can see on the picture with the two additional signals
(2nd and 4th order LP).
von Martin O. (Guest)
Rate this post
useful
not useful
"it seems to work as a high pass (but gives a weird curve as low pass)"
As I did before I would recommend that you implement a testbench to
check every bit of the computation  and compare it for example with an
implementation in lua, java or what so ever. If everything is checked in
that way there will be no more "It seems". It's a little bit of work for
the first filter, but you will easily check other filters afterwards.
Rate this post
useful
not useful
That's what I did, the values look quite nice though and it behaves like
a filter should do (from my understanding).
63336.30075     -126673.25685   63336.30075     -126599.2023    61211.65605     nil
K=      0       Input=  140737488355328 Output= -85901
K=      1       Input=  140737488355328 Output= -85906
K=      2       Input=  140737488355328 Output= -85906
K=      3       Input=  140737488355328 Output= -85906
K=      4       Input=  140737488355328 Output= -85906
K=      5       Input=  140737488355328 Output= -85906
K=      6       Input=  140737488355328 Output= -85906
K=      7       Input=  140737488355328 Output= -85906
K=      8       Input=  140737488355328 Output= -85906
K=      9       Input=  140737488355328 Output= -85906
K=      10      Input=  140737488355328 Output= -85906
K=      11      Input=  140737488355328 Output= -85906
K=      12      Input=  140737488355328 Output= -85906
K=      13      Input=  140737488355328 Output= -85906
K=      14      Input=  140737488355328 Output= -85906
K=      15      Input=  140737488355328 Output= -85906
K=      16      Input=  140737488355328 Output= -85906
K=      17      Input=  140737488355328 Output= -85906
K=      18      Input=  140737488355328 Output= -85906
K=      19      Input=  140737488355328 Output= -85906
K=      20      Input=  140737488355328 Output= -85906
23
K=      21      Input=  0       Output= -6
24
K=      22      Input=  0       Output= -1
25
K=      23      Input=  0       Output= -1
26
K=      24      Input=  0       Output= -1
27
K=      25      Input=  0       Output= -1
28
K=      26      Input=  0       Output= -1
29
K=      27      Input=  0       Output= -1
30
K=      28      Input=  0       Output= -1
31
K=      29      Input=  0       Output= -1
32
K=      30      Input=  0       Output= -1
33
K=      31      Input=  0       Output= -1
34
K=      32      Input=  0       Output= -1
35
K=      33      Input=  0       Output= -1
36
K=      34      Input=  0       Output= -1
37
K=      35      Input=  0       Output= -1
38
K=      36      Input=  0       Output= -1
39
K=      37      Input=  0       Output= -1
40
K=      38      Input=  0       Output= -1
41
K=      39      Input=  0       Output= -1
42
K=      40      Input=  140737488355328 Output= -85901
43
K=      41      Input=  140737488355328 Output= -85906
44
K=      42      Input=  140737488355328 Output= -85906
45
K=      43      Input=  140737488355328 Output= -85906
46
K=      44      Input=  140737488355328 Output= -85906
47
K=      45      Input=  140737488355328 Output= -85906
48
K=      46      Input=  140737488355328 Output= -85906
49
K=      47      Input=  140737488355328 Output= -85906
50
K=      48      Input=  140737488355328 Output= -85906
51
K=      49      Input=  140737488355328 Output= -85906
52
K=      50      Input=  140737488355328 Output= -85906
53
K=      51      Input=  140737488355328 Output= -85906
54
K=      52      Input=  140737488355328 Output= -85906
55
K=      53      Input=  140737488355328 Output= -85906
56
K=      54      Input=  140737488355328 Output= -85906
57
K=      55      Input=  140737488355328 Output= -85906
58
K=      56      Input=  140737488355328 Output= -85906
59
K=      57      Input=  140737488355328 Output= -85906
60
K=      58      Input=  140737488355328 Output= -85906
61
K=      59      Input=  140737488355328 Output= -85906
62
K=      60      Input=  140737488355328 Output= -85906
: Edited by User
Rate this post
useful
not useful
So I did a new VHDL Testbench and my simulation shows that both
implementations are not as equal as I've thought with the jumps as test
values. I'm using a DDS with 100KHz and full amplitude as Input. As you
can see in the picture, the DF1 has kind of a sign in it, which should
explain the behaviour of the filter. Now I need to find out why this is
Rate this post
useful
not useful
It's probably not sufficient to qualitatively compare output values.
I know it's a pain, but sometimes it's the only cure: Compare every bit
of every arithmetic operation and variable for some (initial) steps.
Rate this post
useful
not useful
It seems that an overflow is happening in the simulation, since the most
negative part of the sine is folded to a positive value.
Rate this post
useful
not useful
module biquad1
   parameter coeffWidth = 1,
   parameter productWidth = 1,
   parameter sig1Width = 1
   output wire       [sig1Width-1: 0]  IIRoutput_o ,
   input                                IIRclk_i ,
   input wire                           modeReset_i ,
   input wire  signed [sig1Width-1: 0]  IIRinput_i  ,
   input wire  signed [coeffWidth-1: 0] b0_i ,
   input wire  signed [coeffWidth-1: 0] b1_i ,
   input wire  signed [coeffWidth-1: 0] b2_i ,
   input wire  signed [coeffWidth-1: 0] NEGa1_i ,
   input wire  signed [coeffWidth-1: 0] NEGa2_i
reg  signed [sig1Width-1: 0] s1 ;
reg  signed [sig1Width-1: 0] s2 ;
wire signed [sig1Width-1: 0] vk ;
24
reg  signed [sig1Width-1: 0] vkReg ;
25
reg  signed [sig1Width-1: 0] xk ;
26
reg  signed [sig1Width-1: 0] v1 ;
27
reg  signed [sig1Width-1: 0] v2 ;
28
reg  signed [sig1Width-1: 0] ykReg ;
29
30
wire signed [productWidth-1: 0] productB0;
31
wire signed [productWidth-1: 0] productB1 ;
32
wire signed [productWidth-1: 0] productB2 ;
33
wire signed [productWidth-1: 0] productA1;
34
wire signed [productWidth-1: 0] productA2 ;
35
36
assign vk = IIRinput_i+s1 ;
37
assign productA2 = NEGa2_i*vk ;
38
assign productA1 = NEGa1_i*vk ;
39
assign productB0 = b0_i*vkReg ;
40
assign productB1 = b1_i*vkReg ;
41
assign productB2 = b2_i*vkReg ;
42
43
wire sampleStrobe ;
44
assign sampleStrobe  = 1 ;
45
assign  IIRoutput_o = ykReg ;
46
47
always @(posedge  IIRclk_i ) begin
48
  if ( sampleStrobe ) begin
49
    xk <= IIRinput_i  ;
50
    if ( modeReset_i ) begin
51
      s1<=25'h0 ;
52
      s2<=25'h0 ;
53
      v1<=25'h0 ;
54
      v2<=25'h0 ;
55
      vkReg <= 0 ;
56
      ykReg <= 0 ;
57
      end
58
     else begin
59
      s1<=s2+  productA1[25-1+16:0+16] ;
60
      s2<=     productA2[25-1+16:0+16] ;
61
      v1<=v2 + productB1[25-1+16:0+16]  ;
62
      v2<=     productB2[25-1+16:0+16] ;
63
      vkReg <= vk ;
64
      ykReg <= v1 + productB0[25-1+16:0+16] ;
65
      end
66
    end
67
  end
So sieht meine IIR-Biquad Berechnung in Verilog aus. Mi jedem Takt wird
ein Sample berechnet.
Rate this post
useful
not useful
Did something like that before, this is still directform 1 with just
some async calculations and the filter curves look the same as with my
state machine implementation. Maybe I'll try your implementation of the
DF2, but as far as I can see there is no overflow in the registers, even
with 8 guard bits there seems to be no issue. Can you provide a proper
testbench for your filter?
LIBRARY ieee;
USE ieee.std_logic_1164.ALL;
use ieee.NUMERIC_STD.ALL;
use ieee.std_logic_signed.all;
entity IIRDF1 is
    generic (
        INPUT_WIDTH : integer := 64;
        QFORMAT    : integer := 30;
        B0 : integer := 409494;
        B1 : integer := 818988;
        B2 : integer := 409494;
        A1 : integer := -3954428;
        A2 : integer := 1398100
    port (
        iCLK            : in std_logic;
        iRESET_N        : in std_logic;
        inewValue       : in std_logic;                                 -- indicates a new input value
        iIIR_RX         : in std_logic_vector (INPUT_WIDTH-1 downto 0); -- singed is expected
23
        oDone           : out std_logic;                                -- Done Flag for next Filter
24
        oIIR_TX         : out std_logic_vector (INPUT_WIDTH-1 downto 0)-- Output
25
26
end entity IIRDF1;
27
28
architecture BEH_FixCoefficientIIR of IIRDF1 is
29
30
constant cA1 : signed(QFORMAT+1 downto 0)  := to_signed(A1,QFORMAT+2);-- A1
31
constant cA2 : signed(QFORMAT+1 downto 0)  := to_signed(A2,QFORMAT+2);-- A2
32
constant cB0 : signed(QFORMAT+1 downto 0)  := to_signed(B0,QFORMAT+2);-- B1
33
constant cB1 : signed(QFORMAT+1 downto 0)  := to_signed(B1,QFORMAT+2);-- B1
34
constant cB2 : signed(QFORMAT+1 downto 0)  := to_signed(B2,QFORMAT+2);-- B1
35
36
signal productA1,productA2,productB1,productB2,productB0 : std_logic_vector(INPUT_WIDTH+1+QFORMAT+2 downto 0) := (others => '0');
37
signal nZX0,nZX1,nZX2,nZY1,nZY2 : std_logic_vector(INPUT_WIDTH+1 downto 0) := (others => '0');
38
39
begin
40
productB0 <= std_logic_vector(cB0 * signed(nZX0));
41
productB1 <= std_logic_vector(cB1 * signed(nZX1));
42
productB2 <= std_logic_vector(cB2 * signed(nZX2));
43
productA1 <= std_logic_vector(cA1 * signed(nZY1));
44
productA2 <= std_logic_vector(cA2 * signed(nZY2));
45
46
47
begin
48
    if(rising_edge(iCLK)) then
49
50
51
52
53
            nZY1                <= (others => '0');
54
            nZY2                <= (others => '0');
55
        else
56
            oDone <= '0';
57
            if(inewValue = '1') then
58
                nZX0            <= iIIR_RX(iIIR_RX'left) & iIIR_RX(iIIR_RX'left) & iIIR_RX;
59
                nZX1            <= nZX0;
60
                nZX2            <= nZX1;
61
                nZY1            <= productB0(productB0'left-2 downto QFORMAT)+productB1(productB1'left-2 downto QFORMAT)+productB2(productB2'left-2 downto QFORMAT)-productA1(productA1'left-2 downto QFORMAT)-productA2(productA2'left-2 downto QFORMAT);
62
                oIIR_TX         <= productB0(productB0'left-4 downto QFORMAT)+productB1(productB1'left-4 downto QFORMAT)+productB2(productB2'left-4 downto QFORMAT)-productA1(productA1'left-4 downto QFORMAT)-productA2(productA2'left-4 downto QFORMAT);
63
                nZY2            <= nZY1;
64
                oDone           <= '1';
65
            end if;
66
        end if;
67
    end if;
68
end process;
69
70
end architecture;
Rate this post
useful
not useful
So sieht meine Testbench aus. Die Koeffizienten sind besonders einfach
und ich teste damit die grundlegende Arithmetik. Ob Überläufe
stattfinden teste ich immer am echten Objekt. Das theoretisch im
Vorhinein zu machen ist für mich schwierig, weil ich nicht weiss, welche
Eingangssequenz die "gefährlichste" ist.
module IIR1_tb;
reg TBclk ;
parameter tck = 10; ///< clock tick
always #(tck/2) TBclk <= ~TBclk; // clocking device
integer fd ;
parameter productWidth = 42 ;
parameter coeffWidth = 18 ;
parameter sig1Width = 25 ;
reg  signed [sig1Width-1: 0] IIR1inPrepare ;
reg  signed [sig1Width-1: 0] IIR1in ;
wire signed [sig1Width-1: 0] IIR1out ;
reg [ 32-1: 0] debug1 ;
wire sampleStrobe ;
reg [ 8-1: 0] timer ;
always @(posedge TBclk) begin
23
24
    IIR1in  <=  IIR1inPrepare ;
25
    debug1 <= IIR1out ;
26
  timer <= timer+1 ;
27
    end
28
  end
29
30
reg signed [coeffWidth-1: 0] IIR1b0 ;
31
reg signed [coeffWidth-1: 0] IIR1b1 ;
32
reg signed [coeffWidth-1: 0] IIR1b2 ;
33
reg signed [coeffWidth-1: 0] IIR1a1 ;
34
reg signed [coeffWidth-1: 0] IIR1a2 ;
35
36
reg modeReset ;
37
38
red_pitaya_asg_biquad1
39
40
  .coeffWidth ( coeffWidth ),
41
  .productWidth (productWidth),
42
  .sig1Width (sig1Width )
43
) biquadModule1
44
( .IIRoutput_o ( IIR1out   ) ,
45
  .IIRclk_i    ( TBclk ) ,
46
  .modeReset_i ( modeReset ) ,
47
  .IIRinput_i  ( IIR1in    ) ,
48
  .b0_i        ( IIR1b0    ) ,
49
  .b1_i        ( IIR1b1    ) ,
50
  .b2_i        ( IIR1b2    ) ,
51
  .a1_i        ( IIR1a1    ) ,
52
  .a2_i        ( IIR1a2    )
53
54
55
56
   $fwrite(fd, "TBdout1=%3d TBdout2=%3d TBrst1=%1d TBrst2=%1d\n",
57
       TBdout1,TBdout2,TBrst1,TBrst2) ;
58
  end
59
60
61
initial begin
62
    fd = $fopen("output.txt", "w");
63
64
  $dumpfile("test1.vcd");
65
  $dumpvars(-1, IIR1_tb);
66
  $monitor("%d in=%10d out=%10d ",timer, IIR1in ,IIR1out );
67
  //$monitor("%d in=%10d vk=%10d vkReg=%10d",timer, IIR1in ,vk,vkReg );
68
end
69
70
reg  signed [sig1Width-1: 0] in1 ;
71
reg  signed [sig1Width-1: 0] in2 ;
72
reg  signed [sig1Width-1: 0] in3 ;
73
74
  in1<=IIR1in ;
75
  in2<=in1 ;
76
  end
77
78
79
  in3<=in2 ;
80
  end
81
real rho ;
82
real cosphi ;
83
// testbench actions
84
initial begin
85
  timer=0 ;
86
 // IIR1b0=1<<16 ;  // 1.0
87
 // IIR1b1=( 0) ;
88
 // IIR1b2=( 0)  ;
89
90
91
92
  IIR1b1=(  (1.0)*(2**16)) ;
93
  IIR1b2=( -(0.5)*(2**16))  ;
94
95
//  rho=0.5 ;
96
//  cosphi=-0.5 ;
97
//  IIR1a1= ((-2*cosphi*rho)*(2**16)) ;
98
//  IIR1a2= ((rho*rho)*(2**16)) ;
99
100
101
  IIR1a1= ((-1.0)*(2**16)) ;  // cos phi=sqrt(2)/2
102
  IIR1a2= ((0.5)*(2**16)) ;  // rho=sqrt(2)/2
103
104
 // IIR1a1= 0 ;
105
 // IIR1a2= 0 ;
106
  IIR1inPrepare  <= 0 ;
107
  TBclk = 0;
108
            modeReset = 0;
109
  #(tck);  modeReset = 1;
110
  repeat(5) @(posedge TBclk);
111
  #(tck);  modeReset = 0;
112
113
   @(negedge TBclk);
114
 // IIR1in <= (1<<23) ;
115
   IIR1inPrepare <= (1600000) ;
116
   @(negedge TBclk);
117
118
  repeat(50) @(posedge TBclk);
119
  $fclose(fd);
120
  $finish;
121
122
end
123
124
endmodule
Please log in before posting. Registration is free and takes only a minute.